Re: data input with connection in CustomFB [message #1822578 is a reply to message #1822576] |
Tue, 10 March 2020 08:54 |
joy woo Messages: 198 Registered: May 2019 |
Senior Member |
|
|
This is the attachment, i didn't pack all the template fbs, just my own
After deploying, i just triger the First FB's Req event by manually.
-
Attachment: M35.7z
(Size: 5.19KB, Downloaded 65 times) -
Attachment: 1.jpg
(Size: 29.81KB, Downloaded 69 times) -
Attachment: 2.jpg
(Size: 28.52KB, Downloaded 62 times) -
Attachment: noconn1.jpg
(Size: 27.00KB, Downloaded 67 times) -
Attachment: noconn2.jpg
(Size: 27.52KB, Downloaded 66 times)
[Updated on: Tue, 10 March 2020 09:00] Report message to a moderator
|
|
|
|
|
|
Re: data input with connection in CustomFB [message #1822602 is a reply to message #1822598] |
Tue, 10 March 2020 12:34 |
|
this is perfectly correct behavior of 4diac FORTE. The value that you see is the value at the FB's data store. However this is not the value available for other FBs, as it is defined in IEC 61499. The value is only made available when you send an event. In 4diac FORTE this is solved such that we have a data buffer in the connection. On the occurrence of the output event the FB's value is copied to the connection. On the occurrence of the input event the value is copied from the connection to the value.
When we implemented the monitoring we discussed a long time what values we should show to the users. After weighing all the pros and cons we decided to always show the values at the FB. Although this may lead to a strange situation like in your case you always get the values that are available in your FB for ECC and Algorithms. Maybe we should add a feature to monitor the connection. But I'm not sure if this adds any value.
|
|
|