Home » Eclipse Projects » 4DIAC - Framework for Distributed Industrial Automation and Control » How to create IEC 61131-3 callable function in 4diac?
How to create IEC 61131-3 callable function in 4diac? [message #1863567] Sat, 10 February 2024 12:28 Go to next message
IEC 61131-3 SECANTF function:
FUNCTION SECANTF : REAL
  VAR_INPUT
    X : REAL;
    Y : REAL;
    P : UINT;
  END_VAR
  (* Ketut Kumajaya, 20/08/2018 *)
  (* Reference: https://lar.bnl.gov/properties/basic.html *)
  (* Reference: http://edge.rit.edu/edge/P07106/public/Nox.pdf *)
  IF (P = 3) THEN SECANTF := -Y + 4.863 * EXP((-5.9409785*(1.0 - X) + 1.3553888*EXPT(1.0 - X,1.5) - 0.46497607*EXPT(1.0 - X,2) - 1.5399043*EXPT(1.0 - X,4.5))/X);
    ELSE IF (P = 5) THEN SECANTF := -Y + 7251.0 * EXP((-6.71893 * (1.0 - X) + 1.35966 * EXPT((1.0 - X),1.5) - 1.3779 * EXPT((1.0 - X),2.5) - 4.051 * EXPT((1.0 - X),5))/X);
      ELSE SECANTF := 0.0;
    END_IF;
  END_IF;
END_FUNCTION
IEC 61131-3 SECANT function than call SECANTF function:
FUNCTION SECANT : REAL
  VAR_INPUT
    X1 : REAL;
    X2 : REAL;
    E1 : REAL;
    Y1 : REAL;
    P1 : UINT;
  END_VAR
  VAR
    XM1 : REAL;
    X0 : REAL;
    C1 : REAL;
  END_VAR
  (* Adapted from: https://www.geeksforgeeks.org/program-to-find-root-of-an-equations-using-secant-method/ *)
  XM1 := E1 + 0.1; (* make sure to initially enter the loop *)
  IF (SECANTF(X1,Y1,P1) * SECANTF(X2,Y1,P1) < 0.0) THEN
    (* repeat the loop until the convergence *)
    WHILE (ABS(XM1 - X0) >= E1) DO
      (* calculate the intermediate value *)
       X0 := (X1 * SECANTF(X2,Y1,P1) - X2 * SECANTF(X1,Y1,P1)) / (SECANTF(X2,Y1,P1) - SECANTF(X1,Y1,P1));
      (* check if x0 is root of equation or not *)
      C1 := SECANTF(X1,Y1,P1) * SECANTF(X0,Y1,P1);
      (* update the value of interval *)
      X1 := X2;
      X2 := X0;
      (* if x0 is the root of equation then break the loop *)
      IF (C1 = 0.0) THEN
        EXIT;
      END_IF;
      XM1 := (X1 * SECANTF(X2,Y1,P1) - X2 * SECANTF(X1,Y1,P1)) / (SECANTF(X2,Y1,P1) - SECANTF(X1,Y1,P1));
    END_WHILE;
    SECANT := X0;
  ELSE
    SECANT := 0.0;
  END_IF;
END_FUNCTION
IEC 61499 SECANTF FB:
ALGORITHM calculate
IF (QI = 3) THEN (* argon function *)
	OUT := -Y + 4.863 * EXP((-5.9409785 * (1.0 - X) + 1.3553888 * EXPT(1.0 - X, 1.5) - 0.46497607 * EXPT(1.0 - X, 2) - 1.5399043 * EXPT(1.0 - X, 4.5)) / X);
ELSE
	IF (QI = 5) THEN (* nitrous oxide function *)
		OUT := -Y + 7251.0 * EXP((-6.71893 * (1.0 - X) + 1.35966 * EXPT((1.0 - X), 1.5) - 1.3779 * EXPT((1.0 - X), 2.5)	- 4.051 * EXPT((1.0	- X), 5)) / X);
	ELSE
		OUT := 0.0;
	END_IF;
END_IF;
END_ALGORITHM
IEC 61499 SECANT FB that call SECANTF FB. SECANTF1 is a SECANTF function block type registered inside SECANT FB:
ALGORITHM calculate
(* IF (SECANTF(QI, X1, Y1) * SECANTF(QI, X2, Y1) < 0.0) THEN *)
SECANTF1(QI := QI, X := X1, Y := Y1);
Z1 := SECANTF1.OUT;
SECANTF1(QI := QI, X := X2, Y := Y1);
Z1 := Z1 * SECANTF1.OUT;
IF (Z1 < 0.0) THEN
		(* X0 := (X1 * SECANTF(QI, X2, Y1) - X2 * SECANTF(QI, X1, Y1)) / (SECANTF(QI, X2, Y1) - SECANTF(QI, X1, Y1)); *)
		Z1 := X1 * SECANTF1.OUT;
		Z1 := Z1 - X2 * SECANTF1.OUT;
		X0 := SECANTF1.OUT;
		X0 := X0 - SECANTF1.OUT;
		X0 := Z1 / X0;
		(* C1 := SECANTF(QI, X1, Y1) * SECANTF(QI, X0, Y1) *)
		C1 := SECANTF1.OUT;
		SECANTF1(QI := QI, X := X0, Y := Y1);
		C1 := C1 * SECANTF1.OUT;
		X1 := X2;
		X2 := X0;
		IF (C1 = 0.0) THEN
			EXIT;
		END_IF;
		(* XM1 := (X1 * SECANTF(QI, X2, Y1) - X2 * SECANTF(QI, X1, Y1)) / (SECANTF(QI, X2, Y1) - SECANTF(QI, X1, Y1)); *)
		XM1 := SECANTF1.OUT;
		XM1 := XM1 - SECANTF1.OUT;
		XM1 := Z1 / XM1;
	END_WHILE;
	OUT := X0;
ELSE
	OUT := 0.0;
END_IF;
END_ALGORITHM
Is my implementation above correct or is there any a simpler way? It looks complicated but works.
EDIT:
I can make a C function call inside exported FB easily but I just want to write my FB completely in ST language.
[Updated on: Sat, 10 February 2024 20:29] by Moderator
Re: How to create IEC 61131-3 callable function in 4diac? [message #1863571 is a reply to message #1863567] Sun, 11 February 2024 06:27 Go to previous messageGo to next message
I think having the code in ST is definitely the better solution then in C. Especially from a maintainability and portability perspective.
As there is lot of math involved I have a hard time to say if it is correct. But I would have some general observations that may help you making your code more readable:
- Functions and Function blocks may not have the same name
- if your function is only used by one function block you can define the function as method inside of the function block.
- It loooks like your SECANTF Function is rather expensive. From what I see you always invoke it with two different parameter sets. Doing this once before all your ifs and storing the results in two variables leads to better performance but also to better readable code.
- why is SECANTF an FB and not a method of SECANT FB? A method can access inputs and outputs of the FB. In your case this means you could avoid the QI parameter which again results in a bit better readability of your code.
I hope this helps.
Re: How to create IEC 61131-3 callable function in 4diac? [message #1863572 is a reply to message #1863571] Sun, 11 February 2024 12:59 Go to previous messageGo to next message
METHOD SECANT_FUNC : REAL
VAR_INPUT
	SECANT_FUNC_X : REAL;
END_VAR
IF (SECANT_F = 3) THEN (* argon function *)
	SECANT_FUNC := -SECANT_Y + 4.863 * EXP((-5.9409785 * (1.0 - SECANT_FUNC_X) + 1.3553888 * EXPT(1.0 - SECANT_FUNC_X,
	1.5) - 0.46497607 * EXPT(1.0 - SECANT_FUNC_X, 2.0) - 1.5399043 * EXPT(1.0 - SECANT_FUNC_X, 4.5)) / SECANT_FUNC_X);
ELSE
	IF (SECANT_F = 5) THEN (* nitrous oxide function *)
		SECANT_FUNC := -SECANT_Y + 7251.0 * EXP((-6.71893 * (1.0 - SECANT_FUNC_X) + 1.35966 * EXPT((1.0 - SECANT_FUNC_X)
		, 1.5) - 1.3779 * EXPT((1.0 - SECANT_FUNC_X), 2.5) - 4.051 * EXPT((1.0 - SECANT_FUNC_X), 5)) / SECANT_FUNC_X);
	ELSE
		SECANT_FUNC := 0.0; (* for future function *)
	END_IF;
END_IF;
END_METHOD
METHOD SECANT : REAL
VAR_INPUT
	SECANT_X1 : REAL;
	SECANT_X2 : REAL;
	SECANT_E : REAL;
END_VAR
VAR_TEMP
	SECANT_XM : REAL;
	SECANT_X0 : REAL;
	SECANT_C : REAL;
	SECANT_X11 : REAL;
	SECANT_X21 : REAL;
END_VAR
SECANT_X11 := SECANT_X1; (* to avoid writing to input variable *)
SECANT_X21 := SECANT_X2; (* to avoid writing to input variable *)
SECANT_XM := SECANT_E + 0.1; (* make sure to initially enter the loop *)
IF (SECANT_FUNC(SECANT_X11) * SECANT_FUNC(SECANT_X21) < 0.0) THEN
	WHILE (ABS(SECANT_XM - SECANT_X0) >= SECANT_E) DO
		SECANT_X0 := (SECANT_X11 * SECANT_FUNC(SECANT_X21) - SECANT_X21 * SECANT_FUNC(SECANT_X11)) / (SECANT_FUNC(
		SECANT_X21)
			- SECANT_FUNC(SECANT_X11));
		(* check if SECANT_X0 is root of equation or not *)
		SECANT_C := SECANT_FUNC(SECANT_X11) * SECANT_FUNC(SECANT_X0);
		SECANT_X11 := SECANT_X21;
		SECANT_X21 := SECANT_X0;
		(* if SECANT_X0 is the root of equation then break the loop *)
		IF (SECANT_C = 0.0) THEN
			EXIT;
		END_IF;
		SECANT_XM := (SECANT_X11 * SECANT_FUNC(SECANT_X21) - SECANT_X21 * SECANT_FUNC(SECANT_X11)) / (SECANT_FUNC(
		SECANT_X21)
	END_WHILE;
	SECANT := SECANT_X0;
ELSE
	SECANT := 0.0;
END_IF;
END_METHOD
ALGORITHM calculate
Y1 := Y1 + 1.01325; (* absolute pressure *)
SECANT_Y := Y1 / 10.0;
SECANT_F := 3;
Y1 := -273.15 + SECANT(0.55615813, 1.0, 0.000001) * 150.687;
END_ALGORITHM
My function block implementation much better now. I set SECANT_F and SECANT_Y variable first and then call SECANT method per as your recommendation. Thank you very much.
[Updated on: Sun, 11 February 2024 20:31] by Moderator
Re: How to create IEC 61131-3 callable function in 4diac? [message #1863573 is a reply to message #1863572] Sun, 11 February 2024 15:44 Go to previous messageGo to next message
Great! Happy to help!
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872288 is a reply to message #1863573] Sun, 27 October 2024 07:19 Go to previous messageGo to next message
Hello everyone, I feel enormously dumb, but where do you define FUNCTIONs, METHODs and ALGORITHMs ? I don't find any place in the interface to do that ! It seems you can define global functions and local (i.e. FB local) methods... how ?
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872291 is a reply to message #1872288] Sun, 27 October 2024 08:09 Go to previous messageGo to next message
you do that as part of the textual syntax. in IEC 61131-3 where this syntax is coming from you define blocks of VAR_INPUT ... END_VAR VAR_OUTPUT ... END_VAR. Our code completion should guide you. Or you can also find quite some information on IEC 61131-3 interface specification in Structured TExt in the web.
[Updated on: Sun, 27 October 2024 14:14] by Moderator
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872383 is a reply to message #1872291] Wed, 30 October 2024 04:00 Go to previous messageGo to next message
Ah, now I see the problem ! I was using the official version of the IDE (the one provided on the download page), which lacks a lot of features !
Now I built the "develop" branch from source, and I find all the features you mention.
I have a question about branches though... I see the following:
develop
freeze
release
3.0.x
What is the meaning of these branches ? I suppose "develop"is the curring edge branch, what's the difference between freeze and release ?
I hope you will provide updated binary installers soon, the new version is way better than the "official" one.
Ah, final question: is there some sort of compatibility mapping between IDE and FORTE branches / commits ?
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872395 is a reply to message #1872383] Wed, 30 October 2024 06:05 Go to previous messageGo to next message
Yes the develop branch is the branch where we do all the developments. There it can happen that stuff break or are not working.
The release branch is the current release.
The freeze branch is a branch which we use to test and stabilize features for our prerelease branch. This is the 3.0.x which holds the rather stable version for the next release.
The 4diac FORTE branches with the same name should be compatible to the 4diac IDE branches.
We are heavily working on the upcoming 3.0.0 release. The reason why it is not yet a public release is that there are a few breaking changes upcoming for 4diac FORTE and the 3.0.0 release should have a stable 4diac FORTE API that will be fixed for many years.
I hope this clarifies the situation.
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872407 is a reply to message #1872395] Wed, 30 October 2024 07:30 Go to previous messageGo to next message
Ok, thanks !
When trying to build the release branch I see a strange problem, the build process freezes after a few seconds:
[INFO] Scanning for projects...
[WARNING] The POM for org.apache.commons:commons-lang3:jar:3.8.1 is invalid, transitive dependencies (if any) will not be available: 1 problem was encountered while building the effective model for org.apache.commons:commons-lang3:3.8.1
[FATAL] Non-parseable POM /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/47/commons-parent-47.pom: UTF-8 BOM plus xml decl of ISO-8859-1 is incompatible (position: START_DOCUMENT seen <?xml version="1.0" encoding="ISO-8859-1"... @1:42) @ /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/47/commons-parent-47.pom, line 1, column 42
[WARNING] The POM for commons-io:commons-io:jar:2.5 is invalid, transitive dependencies (if any) will not be available: 1 problem was encountered while building the effective model for commons-io:commons-io:2.5
[FATAL] Non-parseable POM /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/39/commons-parent-39.pom: UTF-8 BOM plus xml decl of ISO-8859-1 is incompatible (position: START_DOCUMENT seen <?xml version="1.0" encoding="ISO-8859-1"... @1:42) @ /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/39/commons-parent-39.pom, line 1, column 42
[WARNING] The POM for commons-io:commons-io:jar:2.6 is invalid, transitive dependencies (if any) will not be available: 1 problem was encountered while building the effective model for commons-io:commons-io:2.6
[FATAL] Non-parseable POM /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/42/commons-parent-42.pom: UTF-8 BOM plus xml decl of ISO-8859-1 is incompatible (position: START_DOCUMENT seen <?xml version="1.0" encoding="ISO-8859-1"... @1:42) @ /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/42/commons-parent-42.pom, line 1, column 42
[WARNING] The POM for org.apache.commons:commons-compress:jar:1.20 is invalid, transitive dependencies (if any) will not be available: 1 problem was encountered while building the effective model for org.apache.commons:commons-compress:1.20
[FATAL] Non-parseable POM /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/48/commons-parent-48.pom: UTF-8 BOM plus xml decl of ISO-8859-1 is incompatible (position: START_DOCUMENT seen <?xml version="1.0" encoding="ISO-8859-1"... @1:42) @ /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/48/commons-parent-48.pom, line 1, column 42
[WARNING] The POM for org.apache.commons:commons-exec:jar:1.3 is invalid, transitive dependencies (if any) will not be available: 1 problem was encountered while building the effective model for org.apache.commons:commons-exec:1.3
[FATAL] Non-parseable POM /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/35/commons-parent-35.pom: UTF-8 BOM plus xml decl of ISO-8859-1 is incompatible (position: START_DOCUMENT seen <?xml version="1.0" encoding="ISO-8859-1"... @1:42) @ /home/gpiasenza/.m2/repository/org/apache/commons/commons-parent/35/commons-parent-35.pom, line 1, column 42
[WARNING] The POM for org.apache.commons:commons-compress:jar:sources:1.20 is invalid, transitive dependencies (if any) will not be available: 1 problem was encountered while building the effective model for org.apache.commons:commons-compress:1.20
[INFO] Computing target platform for MavenProject: org.eclipse.fordiac:org.eclipse.fordiac.ide.product:2.0.1-SNAPSHOT @ /home/gpiasenza/WinShare/Download/Automazione/Source/4diac-ide/plugins/org.eclipse.fordiac.ide.product/pom.xml
[WARNING] No system packages found in profile nor toolchain for JRE-1.1, using current JRE system packages.
This can cause faulty dependency resolution, consider adding a definition for a 'jdk' with id=JRE-1.1 in your toolchains.xml
[WARNING] No system packages found in profile nor toolchain for JavaSE-11, using current JRE system packages.
This can cause faulty dependency resolution, consider adding a definition for a 'jdk' with id=JavaSE-11 in your toolchains.xml
[WARNING] No system packages found in profile nor toolchain for JavaSE-15, using current JRE system packages.
This can cause faulty dependency resolution, consider adding a definition for a 'jdk' with id=JavaSE-15 in your toolchains.xml
[WARNING] No system packages found in profile nor toolchain for JavaSE-16, using current JRE system packages.
This can cause faulty dependency resolution, consider adding a definition for a 'jdk' with id=JavaSE-16 in your toolchains.xml
[WARNING] No system packages found in profile nor toolchain for JavaSE-17, using current JRE system packages.
This can cause faulty dependency resolution, consider adding a definition for a 'jdk' with id=JavaSE-17 in your toolchains.xml
This does not happen with other branches.
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872431 is a reply to message #1872407] Wed, 30 October 2024 16:27 Go to previous messageGo to next message
I fear that the release branch is currently not building anymore. Fixing that would be more work then we currently think it is worth spending on it. Especially as the upcoming version will be so much better. So we would like to spend our effort in getting the remaining bits and pieces fixed. Therefore we would appreciate especially people testing and evaluating the 3.0.x branch and providing feedback there.
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872437 is a reply to message #1872431] Thu, 31 October 2024 04:44 Go to previous messageGo to next message
Ok, I will try the 3.0.x branch. Which FORTE release should I use with that ? I see the following branches:
remotes/origin/1.10.x
remotes/origin/1.11.x
remotes/origin/1.12.x
remotes/origin/1.13.x
remotes/origin/1.14.x
remotes/origin/1.8.x
remotes/origin/1.9.x
remotes/origin/2.0.x
remotes/origin/HEAD -> origin/release
remotes/origin/develop
remotes/origin/feature/opcua/pubsub
remotes/origin/feature/plcdiac
remotes/origin/freeze
remotes/origin/jcabralmt7/updateCI
remotes/origin/release
So there's no 3.0.x branch on the runtime, should I use "develop" ?
Re: How to create IEC 61131-3 callable function in 4diac? [message #1872482 is a reply to message #1872437] Fri, 01 November 2024 04:20 Go to previous message
As not so much 4diac FORTE development is happening you can either use develop or freeze. As an major change is coming to 4diac FORTE in he next days you maybe better of with freeze. But as you are also working on the code develop should also be fine. But maybe you then want to switch also your IDE to develop so that you get the according code generator changes as well.
Previous Topic:Analysis of LUA problems on IDE 3.0.x + Forte develop
Next Topic:"Internal FBs" in a Basic Function Blocks
Current Time: Wed Sep 17 05:21:00 EDT 2025
Powered by FUDForum. Page generated in 0.09090 seconds